Are detached garages required to have a exterior receptacle (ie. plug in)
Are detached garages required to have a exterior receptacle (ie. plug in)
210.52(G) Basements, Garages, and Accessory Buildings. For one and
two- family dwellings, at least one receptacle outlet shall be
installed in the areas specified in 210.52(G)(1) through (3).
These receptacles shall be in addition to receptacles required
for specific equipment.
(1) Garages. In each attached garage and in each detached
garage with electric power, at least one receptacle outlet shall
be installed in each vehicle bay and not more than 1.7 m
(51∕2 ft) above the floor.
(2) Accessory Buildings. In each accessory building with electric
power.
(3) Basements. In each separate unfinished portion of a basement.