I can not find the Article reguarding Detached Garages at a private residence. From memory I think it said that power is not required but if it is installed it must be 120/240 30A.Can some one give me an Article number to refer to?
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: Detached Garage,Req"d # of circuits

MY local electrical inspectors, here in Montgomery County Maryland, Are a model of competence and even handedness in electrical inspection. They have never written a corrective order or declined approval were I didn't have to say they were right. I have wired multiple detached garages here with single branch circuits when all that was wanted was lighting. I am fairly confident that if there was a requirement for a minimum feeder size they would have bagged me by now. The only place that I have found a minimum sizing for supply to buildings is in 230.79 and that only applies to buildings supplied by there own service. Even there the disconnecting means may be as small as 15 ampere if only a single circuit is supplied.
--
Tom

[ July 14, 2003, 12:17 PM: Message edited by: hornetd ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Detached Garage,Req"d # of circuits

There is no requirement for power at a detached garage. If it is installed then the NEC obvioulsy is followed. It can be a single 15A 120v branch circuit or a 200 amp service. However the size of the service or feeder would have to be sufficient for the connected load.
 

rich000

Senior Member
Re: Detached Garage,Req"d # of circuits

If there is greater than 1 circuit, then a seperate ground rod is also required.
 

jro

Senior Member
Re: Detached Garage,Req"d # of circuits

Richooo why would you need a seperate ground-rod :confused:
 

rich000

Senior Member
Re: Detached Garage,Req"d # of circuits

Grounding electrode required except single circuit with EGC.

250.32 (A) Exception
 

jro

Senior Member
Re: Detached Garage,Req"d # of circuits

Rich000 I still don't see why you would need a seperate ground rod. ;)
 

rich000

Senior Member
Re: Detached Garage,Req"d # of circuits

250.32 Two or More Buildings or Structures Supplied from a Common Service

(A) Grounding Electrode. Where two or more buildings or structures are supplied from a common AC service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (C). Where there are no existing grounding electrode(s), the grounding electrode(s) requires in Part III of this article shall be installed.
 

hurk27

Senior Member
Re: Detached Garage,Req"d # of circuits

Ok here's the code:
look at the bold face

210.52
(G) Basements and Garages. For a one-family dwelling, at least one receptacle outlet, in addition to any provided for laundry equipment, shall be installed in each basement and in each attached garage, and in each detached garage with electric power . See 210.8(A)(2) and (A)(5). Where a portion of the basement is finished into one or more habitable rooms, each separate unfinished portion shall have a receptacle outlet installed in accordance with this section.


250.32 Two or More Buildings or Structures Supplied from a Common Service.
(A) Grounding Electrode. Where two or more buildings or structures are supplied from a common ac service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (C). Where there are no existing grounding electrodes, the grounding electrode(s) required in Part III of this article shall be installed.
Exception: A grounding electrode at separate buildings or structures shall not be required where only one branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non?current-carrying parts of all equipment.

[ July 14, 2003, 11:44 PM: Message edited by: hurk27 ]
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Detached Garage,Req"d # of circuits

jro, grounding electrodes are required at seperate buildings for lighting protection. Lighting does not care if its a 30 amp feeder or 800 amp feeder, single or three phase.
 

jro

Senior Member
Re: Detached Garage,Req"d # of circuits

Mrswib power is not required to be taken to a detached garage, but if there is power taken to it then as Hurk27 states Art. 210.52 (G) comes into effect, also Art.210.70 (A) (2) (a) & (b) apply. As for Art. 250.32 its talking about how to connect to the electrode and the second part is when no electrode is present, which then you referance 250.32 (B) or (C) but it never states that a seperate ground rod has to be installed regardless, which brings up the question if I run 2 or more branch crkts to a detached garage in pvc with an equipment ground along with the supply conductors, and there is a grounding electrode present at the main service am I required to install a groundrod.
 

amp-dude

Member
Re: Detached Garage,Req"d # of circuits

mrswib,

Some cities and counties in California have requirements in their building codes for a 240V, 40A circuit to the garage for an electric car charger for battery-powered cars! So, it's run either 8-2 wg NM cable, or a min 3/4" raceway from the main panel to a 4S box.

Of course, California's requirtement for electric vehicles is as good as dead. The range limitations and cost of battery replacement did in electric vehicles, and hybrids (vehicles with an internal combustion engine and small battery pack running an electric motor) are commercially available. But I bet it takes years, if ever, for the building depts to remove the car charger circuit requirement from their books.

Cliff
 

pierre

Senior Member
Re: Detached Garage,Req"d # of circuits

Section 210.52 only says if the detached garage has electric installed, then you will be required to install at least 1 receptacle, 210.8(A)(2) says that receptacle is required to be GFCI protected.

250.32 (A) requires that the detached garage MUST HAVE a grounding electrode system (for dwellings, the electrode will most likely be ground rods).

250.32(B)(2) states, if one does not run an equipment grounding conductor (EGC), and meets all of the requirements, the Grounded Conductor can be the EGC during ground fault conditions.

225.30 states that a multiwire branch circuit is considered a SINGLE CIRCUIT for the purpose of that section. This is also where the requirement of one feed to a separate building is found.

225.31 Disconnecting means required.

225.39 is where to find the disconnecting rating for separate buildings (230.79 has identical wording for services). Notice how 225.39(B) says "not more than two 2-wire branch circuits". This is in concurrence with 225.30

Pierre
 