The rules on this are the same from commercial to residential.I do mainly commercial work and kinda rough on my resi. stuff.
Not just "drive a ground rod", you need to adhere to 250.32(A), which refers to 250.50. You need a Grounding Electrode System at the detached structure.But, I have a detached garage 10' away and I want to add a 50amp subpanel b/c i'm relocating my electric washer and dryer to the garage. So, do I need to drive a ground rod for my subpanel?? I
roughly 60-70' from the service
But, I have a detached garage 10' away and I want to add a 50amp subpanel
Or just install a "2x4 Bonding jumper" and forget about the rods.
R.I.P Bennie
Or we could go with a 'bucket of earth' as he often said.![]()
I just read his threads and I have to say I really Love that guy!
I had some great emails with him as he got sicker, he and my Dad where both Marines they also passed from the same disease. They were a lot a like in many ways. Bennie sent me one of his early Marine pictures it was pretty cool.
why would you want to supply "garbage" with any electricity?FWIW the NEC would allow any size feeder to this garage, only the disconnecting means needs to be rated 60.
So as extreme example you could have a 2 pole 20 amp breaker at the house, run 12 AWG to the garbage and supply a panel with a back fed 60 amp breaker as the required disconnecting means.
I would drive 2 new rods and be done with it.
See 250.56.