Does a detached garage with only one circuit need a subpanel? I can't find in the NEC where a subpanel is required.
Yes. I read that article. Didn't know if was addressed somewhere else. Thanks.It may be supplied by one, two, or three circuits if they're all from a single MWBC. So if you run one MWBC you're good. More circuits than a single MWBC would require a sub-panel. Take a look at 225.30.
Welcome to the Forum.![]()
Why would you need it elsewhere. There is 250.32(B) but that is really about groundingYes. I read that article. Didn't know if was addressed somewhere else. Thanks.
That implies 240v, no neutral.12/2 with ground, 2 pole breaker in the panel. No ground rods.
That implies 240v, no neutral.![]()
That's what I thought too.He probably meant 12/3 with ground
Does a detached garage with only one circuit need a subpanel? I can't find in the NEC where a subpanel is required.
Does a detached garage with only one circuit need a subpanel? I can't find in the NEC where a subpanel is required.
Need more info. How big of circuit, voltage, phase.
If it's only one circuit why would that matter, are you thinking that the one circuit could be a feeder?