Detached garage

Status
Not open for further replies.

Danielinho

Member
Location
Texas
Occupation
Electrician
I have a question and I hope you can help me. Is a sub panel REQUIRED for a detached garage? I’m trying to find something within the 2020 NEC book, but I can’t find a straight answer.
 
A sub panel would be required if you had more circuits than the number that can be supplied by a single MWBC. So if you 2 or 3 circuits as part of a MWBC you would not need the panel.

Welcome to the Forum. :)
 
A sub panel would be required if you had more circuits than the number that can be supplied by a single MWBC. So if you 2 or 3 circuits as part of a MWBC you would not need the panel.

Welcome to the Forum. :)
Got it. Is there a code reference?
Thanks in advance
 