T transman2 Senior Member Location Brooklet,Ga. Jul 7, 2014 #1 Is Detectable Tape required for a duct bank if conduit buried meets code and is under a paved parking lot that has high traffic and could be uncovered/dug up for future projects.
Is Detectable Tape required for a duct bank if conduit buried meets code and is under a paved parking lot that has high traffic and could be uncovered/dug up for future projects.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 7, 2014 #2 In general the NEC does not require the tape for conduit only direct buried conductors.
iwire Moderator Staff member Location Massachusetts Jul 7, 2014 #3 infinity said: In general the NEC does not require the tape for conduit only direct buried conductors. Click to expand... I think it is limited to direct buried service conductors.
infinity said: In general the NEC does not require the tape for conduit only direct buried conductors. Click to expand... I think it is limited to direct buried service conductors.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 7, 2014 #4 iwire said: I think it is limited to direct buried service conductors. Click to expand... I think that you're correct. I forgot the service conductor part in my post.
iwire said: I think it is limited to direct buried service conductors. Click to expand... I think that you're correct. I forgot the service conductor part in my post.