This is an extraordinarily loaded question, though that might not have been your intent. The simple answer is to look at the 75C column (for type RHW) in Table 310.16, discover that a 500 MCM is good for 380 amps, multiply by 5, and determine the ampacity to be 1900 amps.
So why do I think the question is loaded? Because there are many opinions on the proper way to determine the ampacity of conductors in a ductbank, for those installations that do not EXACTLY match the ductback layout sketches that appear in the NEC. Part of the problem is that there are no tables or sketches for 480 volt systems within the enforceable portion of the NEC. There are tables and sketches in Appendix B, but they provide information and not requirements. Also, none of the tables or sketches deal with 5 parallel conductors.
My professional opinion on this topic is that it requires a formal ?Neher-McGrath? calculation by a licensed engineer. I am not alone in that opinion, but we who hold to it are in a minority. I have used two separate software packages to perform this type of calculation. Neither is cheap; the less expensive of the two costs over $2000. I will mention that the results of such a calculation have always shown the ampacity to be far lower than that derived from 310.16. This might explain why I find myself holding a minority opinion.