When determining the MINIMUM size of a feeder conductor for a specific OCPD do you -- 1. look in Table 310.16 and then apply the derating required by 310.15 (B)(2)(a) or do you -- 2. apply the derating factors to the conductor and then call this your MINIMUM sized conductor. For example, I have a 225 amp feeder that has 5 current carrying conductors (3 ungrounded and two grounded, provided for nonlinear load harmonics). For scenario #1, if I consider the 75?C column #4/0 THWN conductor as my minimum size, then apply 310.15(B)(2)(a) my NEW size is a #300 kcmil. On the other hand, for scenario #2, if I know I have 5 current-carrying conductors and multiply my 225 amp rated OCPD by 125% (the inverse of the required 80% derating), I still get a #300 kcmil conductor, BUT now I consider this my MINIMUM sized required ungrounded conductor. I will not need to increase the size of my equipment grounding conductor to compy with 250.122(B) using the second scenario! The problem really has to do with sizing the EGC to comply with 250.122(B)