Hello,
I was trying to figure out this calculation to make sure I fully understand its steps to get the correct answer
Here is the question
Calculation Example
Determine the feeder capacity needed for a 120/240-volt fastened-in-place appliance load in a dwelling unit for the following:
Appliance Rating Load
Water heater 4000 W, 240 V 4000 VA
Kitchen disposal 1/2 hp, 120 V 1176 VA
Dishwasher 1200 W, 120 V 1200 VA
Furnace motor 1/4 hp, 120 V 696 VA
Attic fan 1/4 hp, 120 V 696 VA
Water pump 1/2 hp, 240 V 1176 VA
STEP 1.
Calculate the total of the six fastened-in-place appliances:
Total load = 4000VA + 1176 Va + 1200 VA +696 VA + 696 VA + 1176 VA =8944 VA
STEP 2.
Because the load is for more than four appliances, apply a demand factor of 75 percent:
8944 VA X 0.75 = 6708 VA
When the question asks
Thanks for helping
I was trying to figure out this calculation to make sure I fully understand its steps to get the correct answer
Here is the question
Calculation Example
Determine the feeder capacity needed for a 120/240-volt fastened-in-place appliance load in a dwelling unit for the following:
Appliance Rating Load
Water heater 4000 W, 240 V 4000 VA
Kitchen disposal 1/2 hp, 120 V 1176 VA
Dishwasher 1200 W, 120 V 1200 VA
Furnace motor 1/4 hp, 120 V 696 VA
Attic fan 1/4 hp, 120 V 696 VA
Water pump 1/2 hp, 240 V 1176 VA
STEP 1.
Calculate the total of the six fastened-in-place appliances:
Total load = 4000VA + 1176 Va + 1200 VA +696 VA + 696 VA + 1176 VA =8944 VA
STEP 2.
Because the load is for more than four appliances, apply a demand factor of 75 percent:
8944 VA X 0.75 = 6708 VA
When the question asks
Is 6708 VA the answer there looking for?Determine the feeder capacity needed for a 120/240-volt fastened-in-place appliance load in a dwelling unit
Thanks for helping