BigBreakfastJohn
New User
- Location
- South Carolina/USA
- Occupation
- EE
Three questions about KVA requirements
Background:
We have a building with a mix of 480V, 208V, and 240V panels. No drawings to speak of, almost all panel schedules are out of date. I'm trying to determine load requirements so we can reroute power to it. It's a lab building with a variety of equipment that runs at random hours for random times, so figuring out power draw from their loads is difficult. I talked to their process engineer, the run-time numbers he gave me seemed way too long.
I also plan to go in the morning before their work day, check the power meter (old style analog, with no ammeter or remote monitoring), and go at the end to see their power draw for a single 8 hour shift.
Daily average KWh for the building is about 1400, but without knowing when they're using the different load, I don't know their peak loads.
Question 1: Is there anything else I do/look at to determine loading?
All of the building's power is supplied from one 480V 100A breaker and one 480V 400A breaker.
Question 2: Is it reasonable to say I need 240KVA of transformer from the utility using this method?
2nd question:
On a walkthrough for re-powering the same building with the utility, the utility engineer said that 3 100 KVA transformers are sufficient for a 300 KVA service.
Question 3: If it's 3 phases, doesn't that just mean that it's 3 phases of 100KVA capacity?
Background:
We have a building with a mix of 480V, 208V, and 240V panels. No drawings to speak of, almost all panel schedules are out of date. I'm trying to determine load requirements so we can reroute power to it. It's a lab building with a variety of equipment that runs at random hours for random times, so figuring out power draw from their loads is difficult. I talked to their process engineer, the run-time numbers he gave me seemed way too long.
I also plan to go in the morning before their work day, check the power meter (old style analog, with no ammeter or remote monitoring), and go at the end to see their power draw for a single 8 hour shift.
Daily average KWh for the building is about 1400, but without knowing when they're using the different load, I don't know their peak loads.
Question 1: Is there anything else I do/look at to determine loading?
All of the building's power is supplied from one 480V 100A breaker and one 480V 400A breaker.
Question 2: Is it reasonable to say I need 240KVA of transformer from the utility using this method?
2nd question:
On a walkthrough for re-powering the same building with the utility, the utility engineer said that 3 100 KVA transformers are sufficient for a 300 KVA service.
Question 3: If it's 3 phases, doesn't that just mean that it's 3 phases of 100KVA capacity?