Scottrandall
- Minneapolis, MN
- Engineer
We are measuring demand in MFH buildings in Minnesota. If measurements occur over cooling season, we see about 104 KW for 48 units or about 2.17 KW per unit. Outside of cooling season we see about 1.65 KW per unit. When we measure outside of cooling season we are forced to calculate A/C demand and add on to measured demand. NEC requires A/C be calculated at 100% of nameplate without demand factor. Each A/C unit is 23 amps at 240 volts or 5.52KW. 48x5.52=265KW. Based our our measured values over a number of jobs we would have expected it to be around 26KW. Calculated versus measured seems to be different by a factor of 10. Is this real or am I missing something?