Determining disconnect size for ac unit

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
If a multimotor ac unit has a MCA of 50 amps and a MOP of 70 amps, how do I determine the rating of the disconnect switch? 115% of the MCA?
 
If a multimotor ac unit has a MCA of 50 amps and a MOP of 70 amps, how do I determine the rating of the disconnect switch? 115% of the MCA?
115% of the mca is what I have used for a/c since that usually has the 125% built in the MCA

440.12 Rating and Interrupting Capacity.
(A) Hermetic Refrigerant Motor-Compressor. A disconnecting
means serving a hermetic refrigerant motor-compressor
shall be selected on the basis of the nameplate rated-load
current or branch-circuit selection current, whichever is
greater, and locked-rotor current, respectively, of the motor compressor
as follows.
(1) Ampere Rating. The ampere rating shall be at least
115 percent of the nameplate rated-load current or branch circuit
selection current, whichever is greater.
 
What is considered the branch circuit selection current? And do you have an example of why they say "whichever is greater".

440.2 Definitions.
Branch-Circuit Selection Current. The value in amperes
to be used instead of the rated-load current in determining
the ratings of motor branch-circuit conductors, disconnecting
means, controllers, and branch-circuit short-circuit and
ground-fault protective devices wherever the running overload
protective device permits a sustained current greater
than the specified percentage of the rated-load current. The
value of branch-circuit selection current will always be
equal to or greater than the marked rated-load current.


I copied this quote from a similar post.

"Branch circuit selection current" and MCA are NOT the same thing. See the definition in 440.2.

See also 440.32. "Branch-circuit conductors supplying a single motor-compressor shall have an ampacity not less than (that is to say, MCA) 125% of either the motor compressor rated load current or branch-circuit selection current.

In other words, MCA = 1.25*RLA or 1.25*BCSC, whichever is greater. MCA does not equal BCSC.
 
Thanks.

That helps a little but I still don't know what branch circuit selection current exactly is. Could you provide an example?

I just know that it is NOT the MCA or the RLA. So why is this a separate definition if all we really care about is the RLA and MCA?
 
Thanks.

That helps a little but I still don't know what branch circuit selection current exactly is. Could you provide an example?

I just know that it is NOT the MCA or the RLA. So why is this a separate definition if all we really care about is the RLA and MCA?

BCSC would be marked on a unit that has a protection system that permits sustained current of greater than 156% of the RLA.

If you had a unit with a BCSC marked on it, you would care about that rather than RLA. I've never seen a unit with a BCSC value.
 
BCSC would be marked on a unit that has a protection system that permits sustained current of greater than 156% of the RLA.

If you had a unit with a BCSC marked on it, you would care about that rather than RLA. I've never seen a unit with a BCSC value.

Thanks!!
 
Wouldn't the branch circuit selection be the overcurrent protective device since that is how the branch circuit is rated

210.3 Rating. Branch circuits recognized by this article shall
be rated in accordance with the maximum permitted ampere
rating or setting of the overcurrent device.
 
Wouldn't the branch circuit selection be the overcurrent protective device since that is how the branch circuit is rated

The overcurrent protective device should not exceed 175% of the branch circuit selection current, or not exceed 225% of the bcsc where the smaller protective device is not sufficient for the starting current of the motor...440.22(A)
 
The overcurrent protective device should not exceed 175% of the branch circuit selection current, or not exceed 225% of the bcsc where the smaller protective device is not sufficient for the starting current of the motor...440.22(A)

Yes I know that. I was saying isn't that the branch circuit selection and the disconnect needed to be 115% of the overcurrent protective device?
 
No, the disco only needs to be rated for 115% of the BCSC. The OCPD is not a factor.

For the nameplate above I could use a 30A disco with a 40A breaker.

I don't think you can use a 30 amp disconnect with a 40 amp breaker. Wouldn't the disconnect have to be rated for the 40 amps.
 
I don't see any problem with a 30A disconnect and a 40A breaker.
If the equipment is rated 30 amp I didn't think a 40 amp breaker was allowed. I realize the load isn't 40 amps. I think about a 30 amp fused disconnect-- you cannot use 40 amp fuses so I assumed the equipment could not have a breaker rated higher than the ampacity of the unit
 