I'm looking at a situation where I need to add a 780A load to an existing 480V Switchboard to feed new chiller loads (780A is calculated new chiller loads). The existing 480V Switchboard is a 1600A rated Switchboards with (3) 800A feeder breakers feeding downstream panels.
I'm trying to determine what the existing load is on this 1600A Switchboard to see if there is enough capacity to add the new chiller loads. The (3) 800A feeder breakrs feed downstream 800A ATS's which in turn feed 800A emergency panels.
I've had not luck tracking down any sort of load schedules for either the 1600A Switchboard or downstream 800A panelboards to give an indication of the existing calculated load. I have the one-lines that show all the feeders from these downstream panels (feeding other panels and loads) but nothing that quantifies loading.
The other option in lieu of any load data would be setting up power monitors at a location to be able to measure the existing loads. Unfortunately the 1600A Switchboard in question is an emergency board and would only have load during emergency gen conditions so we'd likely have to setup (3) meters at the load side of each ATS or the panelboards themselves and then have to manually add loads to quantify total loads.
I'm trying to come up with ideas on how to potentially quantify the existing loads without having to go through the process of metering. I'm curious to hear any ideas how others would approach this?
I'm trying to determine what the existing load is on this 1600A Switchboard to see if there is enough capacity to add the new chiller loads. The (3) 800A feeder breakrs feed downstream 800A ATS's which in turn feed 800A emergency panels.
I've had not luck tracking down any sort of load schedules for either the 1600A Switchboard or downstream 800A panelboards to give an indication of the existing calculated load. I have the one-lines that show all the feeders from these downstream panels (feeding other panels and loads) but nothing that quantifies loading.
The other option in lieu of any load data would be setting up power monitors at a location to be able to measure the existing loads. Unfortunately the 1600A Switchboard in question is an emergency board and would only have load during emergency gen conditions so we'd likely have to setup (3) meters at the load side of each ATS or the panelboards themselves and then have to manually add loads to quantify total loads.
I'm trying to come up with ideas on how to potentially quantify the existing loads without having to go through the process of metering. I'm curious to hear any ideas how others would approach this?