Does anyone actual use this though? To apply a meter and wait 30 days before you can even work or design a space?
I have done so many times. But there are things that you can do while waiting for the results of the 30 day load study. I have approached the AHJ with a request for a preliminary review based on just the first week's worth of data. I then gave the AHJ the final results at the end of the 30 days. You can use other available information sources as the starting point for the design, and either confirm or adjust your design when you know the final results.Does anyone actual use this though? To apply a meter and wait 30 days before you can even work or design a space?
I have done so many times. But there are things that you can do while waiting for the results of the 30 day load study. I have approached the AHJ with a request for a preliminary review based on just the first week's worth of data. I then gave the AHJ the final results at the end of the 30 days. You can use other available information sources as the starting point for the design, and either confirm or adjust your design when you know the final results.
Thanks. Why does the NEC allow 30 days? If testing is done during spring/fall, the AC or heat may not be on or at low cycle compared to summer/winter. And if this low amperage is now used as the basis of design, couldn't this potentially be bad if AC and heat loads aren't incorporated?
If heating and cooling loads are present, one is supposed to account for this possible additional load, although the NEC doesn't specifically say how.
I assume you could just assume the heat or AC was off during the monitoring, and add it as another separate load.