Determining Existing Service Size

Status
Not open for further replies.

Jeffrey_S

New member
Location
Los Angeles, CA
I am an architect (please don't hold that against me :), and I have a question regarding how to determine service size.

How do I determine the approximate electrical service (amperage) to an apartment when there does not seem to be a service disconnect that gives you that information. I am looking at a 47-unit apartment building with a master meter and 400 amps of service. How do I back into figuring out the apporximate amount of power provided to each apartment (no need to be exact)? Thanks for your help here.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't know of a shortcut. As far as the individual apartments I think I would fall back to an Article 220 calculation.
I can't imagine a 47 unit building that does not have a main or multiple mains to give you some idea on existing service sizes.
 
Sounds like you are looking for the capacity of the FEEDER serving each apartment - There is only one electrical service, and one (or a grouped set of up to 6) service disconnect. If that is the case, you would look at the circuit breaker in the distribution equipment that feeds the apartment(s), and I would also check the wire size to double check.
 