determining how many watts a FA speaker circuit is drawing?
neko988
hello, i am in the process of swapping out a bulk audio evac system with 7 class A cicuits. they are run off a 2, 250 watt bulk audio amps. we're installing a FCI E3, with 120watt amps, the question i have is, is there any way of ringing out each cicruit to see how many watts each is drawing (without having to count the number of devices on each, and checking what they are set at). i would really like to have a baseline of each circuit and what its drawing on each amp for future referance. thanks in advance for any help.
Find the resistance of the circuit and take the voltage of the source and plug them into ohm's law.
That should give you a close idea.
Not quite. Assuming he is dealing with speakers, inductive reactance of their coils cannot be simply measured by the DC resistance of the circuit.
I agree with Pete and will add that you would only be reading the primary side of the matching transformers on each speaker.
Not familiar with FA and life safety systems but I have to assume that this is most likely a constant voltage, probably a 70.7 volt system. Even if it isn't, Peter is correct in that DC resistance will tell you nothing. This is an inductive load.
First, you have to determine how this system works then use an audio impedance meter to measure the impedance of each circuit. Then you would use that information and the method of distribution to determine the total power needed.
For instance, if this is a 70 volt system and the total load impedance of all 7 circuits added together is 16 ohms then you will need at least a 300 watt amp.
That said, I would say that if the old system had two 250 watt amps and if what you are replacing it with isn't at least 500 watts total you won't have the proper SPLs and could possibly damage the underpowered amps.
-Hal
They made a piece of equipment (bridge ???) that will measure the watts of a line or circuit. It is like a meter.
yeah, meters like this one.
Alternatively, when the building is clear of people :) connect a sine wave oscillator at 1KHz to the amp, and use a couple of DVMs to simultaneously measure the AC voltage and current on the speaker lines. R=E/I. Dont turn the amp up too far just want a few volts on the line.
Only have one DVM? (but it needs a 2 volt AC range)
Here is one way to measure it.
Use a portable CD player with a test tone CD of 400 or 1000Hz. The DVM doesn't need much accuracy at the test frequency. Let's say that we are testing an 8Ohm system. Remove the speaker wires from the amplifier, connect one end of a 1000 Ohm resistor to the positive speaker terminal, connect one end of a 10 Ohm resistor to the neutral terminal, connect the other ends of both resistors together. Measure the voltage across the 10 Ohm resistor and adjust the signal voltage input until the meter reads 1.0 Volts. This calibrates the meter to read Ohms. 1.0V = 10 Ohm, 0.5V = 5 Ohm, 2.0V = 20 Ohm. Now disconnect the 10 Ohm resistor and connect the speaker wires to the same points and do your measurements.
Audio Circuit Requirements
Neko,
Was this system designed by an engineer from the alarm manufacturer or other similar group such as the electrical engineer for the GC? if not, the AHJ should have asked for that. Then you would have that info. As an AHJ, I always require the relevant calcs before I approve the permit. Depending on the job, it might be battery calcs, audio circuit capacities, voltage drop calcs, etc. Simplex and Seimens are also pretty good about supplying data sheets with some of that info included. I realize I haven't helped you calculate the answer, but I hope I might have pointed out a route to the answer.:confused:
Mike
the new system doesn't have an accurate shop drawing and submittal ? I would think you would be able to determine this info from the cut sheets on the devices you have so that your solution works (unless I'm missing something)