Determining locked rotor current
Ok guys, need further help with this air compressor. The utility is asking for the locked rotor current. I do not see this information anywhere nor a nema code letter on the motor. Here is the motor dataplate.
gadfly56
New Jersey
Professional Engineer, Fire & Life Safety
Isn't the rule-of-thumb 6 or 7 times FLA?
Jraef
Moderator, OTD
Electrical Engineer
That’s not a NEMA compliant nameplate, otherwise it would provide you with the Locked Rotor kVA code number. You could call Weg and ask them for it, but good luck with that.
On something that small, I would just guesstimate it at 600% of FLA.
Yeah, this is a foreign machine I believe
Since I'm in the office I took a quick peek at WEG's web site. This motor is a very odd duck and the closest I could find was this:
http://ecatalog.weg.net/redirect/index.asp?p_Categoria=490&p_Produto=471&p_Table=YES
You'll have to filter to find the 30 HP motors. I picked the one operating at 3,600 RPM.
It lists the locked rotor as "(II/In)=9.5"
What does that mean?
GeorgeB
ElectroHydraulics engineer (retired)
Greenville SC
Retired
II instantaneous current
In normal current
so 9.5x the marked 60 Hz value ... for a SIMILAR motor ... so a good estimate would be that ... but give it as an estimate unless WEG will give you a better number.
gar
Ann Arbor, Michigan
EE
180227-1443 EST
I posted some plots of motor starting current at
http://forums.mikeholt.com/showthread.php?t=174880&highlight=
Essentially locked rotor motor current is the initial starting current of a motor. Basically when you start a motor the rotor is not rotating, essentially locked rotor, and therefore if you measure motor starting current you can determine locked rotor current.
Note from my plots that motor starting current remains high for many cycles.
Besoeker
UK
Not sure if it applies here or not, but in general "high efficiency" motors have higher inrush because of the design changes such as lower winding DC resistance made to increase efficiency.
I agree. When I had to provide system efficiency guaranteed figures at the bid stage I noted the differences. It also impacts on starting/locked rotor currents.
MyCleveland
Cleveland, Ohio
there is a difference between "instantaneous / inrush current" and "locked rotor current".
Jraef: Please expand on this difference...is instantaneous / inrush current a manufacturer design parameter ?
Regarding "LRC", I thought we are directed by 430.110 steering us to use values in back of 430. Is this not the direction for the original question ?
See the link gar posted. It gets into that discussion
My issue is this motor does not have a letter code
Jraef
Moderator, OTD
Electrical Engineer
And I should have added, the PoCo will be interested in Locked Rotor Current because that can have an effect on voltage drop, not the instantaneous/inrush/magnetizing current that only lasts a few cycles.
gadfly56
New Jersey
Per the OP, there is no information on the type of motor, B, C, or D.
E.T.A
Ooops, didn't read far enough down the thread. My bad. :ashamed1: