65Alive
Member
- Location
- Nashville,TN
Friends, I'm new to the forum and am a residential home inspector and mechanical engineer. I typically decline commercial work as I am less familiar but looked at a 6000 SF commercial office building built in 2006 likely to the 2000 IBC for friend who is looking to purchase the building. To be clear we have no intention of doing any electrical work and he will get an electrician when and if needed.
The main breaker of the service is an 800 max. Seimans Sentron Series unit Model # MD63F800. It is a 3 phase system with 2-350 kcmil copper wires entering all 3 lugs. Depending on the wire temp rating it looks like the 350 service wiring is rated at 310/350 Amps x2 would be 610/700 Amps which is not up to the 800 breaker protection. I am sure this is not the correct way to look at this. Also I see 3 dials at the lower section of the breaker graduated from 1low to 8high...which are all set at 1low. Is the amp rating of the breaker adjustable using these dials?
Long and short i want to properly report the service size and confirm the compatibility of the service wiring with the over current protection....Thanks in advance...Bill
The main breaker of the service is an 800 max. Seimans Sentron Series unit Model # MD63F800. It is a 3 phase system with 2-350 kcmil copper wires entering all 3 lugs. Depending on the wire temp rating it looks like the 350 service wiring is rated at 310/350 Amps x2 would be 610/700 Amps which is not up to the 800 breaker protection. I am sure this is not the correct way to look at this. Also I see 3 dials at the lower section of the breaker graduated from 1low to 8high...which are all set at 1low. Is the amp rating of the breaker adjustable using these dials?
Long and short i want to properly report the service size and confirm the compatibility of the service wiring with the over current protection....Thanks in advance...Bill