determining service wire size

Status
Not open for further replies.

xara

Member
Location
minneapolis, mn
I noticed 100 amps requires 1 awg aluminum THW wire in table NEC 310.15(b)(16). however, 310.15(b)(7) (dwelling services and feeders) requires 2 gauge Aluminum wire for a 100 amp service. Why do these tables differ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
310.15(B)(7) takes into account the load diversity for dwelling units with the realization the conductor would only see the full load for a short period of time.
In other situations the load diversity would likely not justify the reduced conductor size.
 