C C-Elect New member Oct 12, 2006 #1 If I have a 20 Amp breaker and my distance is 175 ft. away. The maximum operative load is 115 VAC and 9.0 Amps. This operates an ATM machine. Will a #10 AWG wire be sufficient?
If I have a 20 Amp breaker and my distance is 175 ft. away. The maximum operative load is 115 VAC and 9.0 Amps. This operates an ATM machine. Will a #10 AWG wire be sufficient?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Oct 12, 2006 #3 Yes as Bryan said #10 will work just fine. You can try different size conductors here: http://www.electrician2.com/calculators/vd_calculatoradv.htm
Yes as Bryan said #10 will work just fine. You can try different size conductors here: http://www.electrician2.com/calculators/vd_calculatoradv.htm