Device Boxes in a fire wall

Status
Not open for further replies.

gmayeux

Member
this is probably a easy question, I have never been asked this, I am installing 4 square metal boxes in a 2 hour fire wall, applied putty pads where required, on boxes that did not need putty pad's the AHJ asked if the boxes being used are UL fire rated and listed. I don't know, is a standard 4sq box meet that? I looked in the UL white book and cannot find anything.
 
The inspector should know this, yes they are, click HERE

Roger
 
In addition to what Roger posted, the IBC Section 714.3.2 Exception 1. addresses penetrations of a maximum 2 hour rated wall by steel electrical boxes.

Chris
 