Can anyone give me a good resource for finding what specific device numbers represent along with a detailed explanation of functionality? For example, device #51 is an AC Time Overcurrent Relay and that means it does blablablablabla. :)
 
Re: Device Numbers

Device Number Function and Description
1 MASTER ELEMENT is the initiating device, such as a control switch, voltage relay, float switch, etc. which serves either directly or through such permissive devices as protective and time-delay relays to place an equipment in or out of operation.
2 TIME-DELAY STARTING OR CLOSING RELAY is a device that functions to give a desired amount of time delay before or after any point of operation in a switching sequence or protective relay system, except as specifically provided by device functions 48, 62 and 79.
3 CHECKING OR INTERLOCKING RELAY is a relay that operates in response to the position of a number of other devices (or to a number of predetermined conditions) in equipment. It allows an operating sequence to proceed, or to stop, or to provide a check of the position of these devices or of these conditions for any purpose.
4 MASTER CONTRACTOR is a device, generally controlled by device function 1 or the equivalent and the required permissive and protective devices. It serves to make and break the necessary control circuits to place an equipment into operation under the desired conditions and to take it out of operation under other or abnormal conditions.
5 STOPPING DEVICE is a control device used primarily to shut down equipment and hold it out of operation. The device may be manually or electrically actuated but excludes the function of electrical lockout (see device function 86) on abnormal conditions.
6 STARTING CIRCUIT BREAKER is a device whose principal function is to connect a machine to its source of starting voltage.


Device Number Function and Description
7 ANODE CIRCUIT BREAKER is a device used in the anode circuits of a power rectifier for the primary purpose of interrupting the rectifier circuit if an arcback should occur.
8 CONTROL POWER DISCONNECTING DEVICE is a disconnecting device, such as a knife switch, circuit breaker, or pull-out fuse block, used for the purpose of respectively connecting and disconnecting the source of control power to and from the control bus or equipment. Note: Control power is considered to include auxiliary power that supplies such apparatus as small motors and heaters.
9 REVERSING DEVICE is a device that is used for the purpose of reversing a machine field or for performing any other reversing functions.
10 UNIT SEQUENCE SWITCH is a switch that is used to change the sequence in which units may be placed in and out of service in multiple-unit equipment.
11 RESERVED FOR FUTURE APPLICATION.
12 OVER-SPEED DEVICE is usually a direct connected speed switch, which functions on machine over-speed.
13 SYNCHRONOUS-SPEED DEVICE is a device such as a centrifugal-speed switch, a slip-frequency relay, a voltage relay, an undercurrent relay, or any type of device that operates at approximately the synchronous speed of a machine.
14 UNDER-SPEED DEVICE is a device that functions when the speed of a machine falls below a predetermined value.
15 SPEED OR FREQUENCY MATCHING DEVICE is a device that functions to match and hold the speed or the frequency of a machine or of a system equal to, or approximately equal to, that of another machine, source, or system.
16 RESERVED FOR FUTURE APPLICATION.
17 SHUNTING OR DISCHARGE SWITCH is a switch that @ to open or to close a shunting circuit around any piece of apparatus (except a resistor), such as a machine field, a machine armature, a capacitor, or a reactor. Note: This excludes devices that perform such shunting operations as may be necessary in the process of starting a machine by 6 or 42 or their equivalent, and also excludes device function 73 that serves for the switching of resistors.
18 ACCELERATING OR DECELERATING DEVICE is a device that is used to closes or to cause the closing of circuits that are used to increase or decrease the speed of a machine.
19 STARTING-TO-RUNNING TRANSITION CONTACTOR is a device that operates to initiate or cause the automatic transfer of a machine from the starting to the running power connection.
20 VALVE is one used in a vacuum, air, gas, oil, or similar line, when it is electrically operated or has electrical accessories such as auxiliary switches.
21 DISTANCE RELAY is a relay that functions when the circuit admittance, impedance, or reactance increases or decreases beyond predetermined limits.
22 EQUALIZER CIRCUIT BREAKER is a breaker that serves to control or to make and break the equalizer or the current-balancing connection for a machine field, or for regulating equipment, in a multiple-unit installation.


Device Number Function and Description
23 TEMPERATURE CONTROL DEVICE is a device that functions to raise or lower the temperature of a machine or other apparatus, or of any medium, when its temperature falls below, or rises above, a predetermined value.
24 RESERVED FOR FUTURE APPLICATION.
25 SYNCHRONIZING OR SYNCHRONISM-CHECK DEVICE is a device that operates when two a-c circuits arc within the desired limits of frequency, phase angle, or voltage, to permit or to cause the paralleling of these two circuits.
26 APPARATUS THERMAL DEVICE is a device that functions when the temperature of the shunt field or the amortisseur winding of a machine, or that of a load limiting or load shifting resistor or of a liquid or other medium, exceeds a predetermined value. It may also function if the temperature of the protected apparatus, such as a power rectifier, or of any medium decreases below a predetermined value.
27 UNDERVOLTAGE RELAY is a relay that functions on a given value of undervoltage.
28 FLAME DETECTOR is a device that monitors the presence of the pilot or main flame in such apparatus as a gas turbine or a steam boiler.
29 ISOLATING CONTACTOR is a device that is used expressly for disconnecting one circuit from another for the purposes of emergency operation, maintenance, or test.
30 ANNUNCIATOR RELAY is a non-automatically reset device that gives a number of separate visual indications upon the functioning of protective devices, and which may also be arranged to perform a lockout function.
31 SEPARATE EXCITATION DEVICE is a device that connects a circuit, such as the shunt field or synchronous converter, to a source of separate excitation during the starting sequence; or one that energizes the excitation and ignition circuits of a power rectifier.
32 DIRECTIONAL POWER RELAY is a device that functions on a desired value of power flow in a given direction or upon reverse power resulting form arcback in the anode or cathode circuits of a power rectifier.
33 POSITION SWITCH is a switch that makes or breaks contact when the main device or piece of apparatus that has no device functions number reaches a given position.
34 MASTER SEQUENCE DEVICE is a device such as a motor-operated multi-contact switch, or the equivalent, or a programming device, such as a computer, that establishes or determines the operating sequence of the major devices in equipment during starting and stopping or during other sequential switching operations.
35 BRUSH-OPERATING OR SLIP-RING SHORT CIRCUITING DEVICE is a device for raising, lowering, or shifting the brushes of a machine, t for short-circuiting its slip rings, or for engaging or disengaging those contacts of a mechanical rectifier.
36 POLARITY OR POLARIZING VOLTAGE DEVICE is a device that operates or permits the operation of, another device on a predetermined polarity only, or verifies that presence of a polarizing voltage in equipment.


Device Number Function and Description
37 UNDERCURRENT OR UNDER POWER RELAY is a relay that functions when the current or power flow decreases below a predetermined value.
38 BEARING PROTECTIVE DEVICE is a device that functions on excessive bearing temperature, or on other abnormal mechanical conditions associated with the bearing, such as undue wear, which may eventually result in excessive bearing temperature or failure.
39 MECHANICAL CONDITION MONITOR is a device that function upon the occurrence of an abnormal mechanical condition (except that associated with bearings as covered under de-vice function 38), such as excessive vibration, eccentricity, expansion, shock, tilting, or sea] failure.
40 FIELD RELAY is a relay that functions on a given or abnormally low value or failure of machine field current, or on an excessive value of the reactive component of armature current in an a-c machine indicating abnormally low field excitation.
41 FIELD CIRCUIT BREAKER is a device that functions to apply or remove the field excitation of a machine.
42 RUNNING CIRCUIT BREAKER is a device whose principal function is to connect a machine to its source of running or operating voltage. This function may also be used for a device, such as a Contactor, that is used in series with a circuit breaker or other fault protecting means, primarily for frequent opening and closing of the circuit.
43 MANUAL TRANSFER OR SELECTOR DEVICE is a manually operated device that transfers the control circuits in order to modify the plan of operation of the switching equipment or of some of the devices.
44 UNIT SEQUENCE STARTING RELAY is a relay that functions to start the next available unit in a multiple-unit equipment upon the failure or non-availability of the normally preceding unit.
45 ATMOSPHERIC CONDITION MONITOR is a device that functions upon the occurrence of an abnormal atmospheric condition, such as damaging fumes, explosive mixtures, smoke, or fire.
46 REVERSE-PHASE OR PHASE-BALANCE CURRENT RELAY is a relay that functions when the polyphase currents are of reverse-phase sequence, or when the polyphase currents are unbalanced or contain negative phase-sequence components above a given amount.
47 PHASE-SEQUENCE VOLTAGE RELAY is a relay that functions upon a predetermined value of polyphase voltage in the desired phase sequence.
48 INCOMPLETE SEQUENCE RELAY is a relay that generally returns that equipment to the normal, or off, position and locks it out if the normal starting, operating, or stopping sequence is not properly completed within a predetermined time.
49 MACHINE OR TRANSFORMER THERMAL RELAY is a relay that functions when the temperature of a machine armature or other load carrying winding or element of a machine or the temperature of a power rectifier or power transformer (including a power rectifier transformer) exceeds a predetermined value.
50 INSTANTANEOUS OVERCURRENT OR RATE OF-RISE RELAY is a relay that functions instantaneously on an excessive value of current or on an excessive rate of current rise, thus indicating a fault in the apparatus or circuit being protected.
Device Number Function and Description
51 A-C TIME OVERCURRENT RELAY is a relay with either a definite or inverse time characteristic that functions when the current is an ac circuit exceeds a predetermined value.
52 A-C CIRCUIT BREAKER is a device that is used to close and interrupt an a-c power circuit under normal conditions or to interrupt this circuit under fault or emergency conditions.
53 EXCITER OR D-C GENERATOR RELAY is a relay that forces the d-c machine field excitation to guild up during starting or which functions when the machine voltage has been built up to a given value.
54 RESERVED FOR FUTURE APPLICATION.
55 POWER FACTOR RELAY is a relay that operates when the power factor is an a-c circuit rises above or falls below a predetermined value.
56 FIELD APPLICATION RELAY is a relay that automatically controls the application of the field excitation to an a-c motor at some predetermined point in the slip cycle.
57 SHORT-CIRCUITING OR GROUNDING DEVICE is a primary circuit switching device that functions to short-circuit or to ground a circuit in response to automatic or manual means.
58 RECTIFICATION FAILURE RELAY is a device that functions if one or more anodes of a power rectifier fail to fire, or to detect an arc-back or on failure of a diode to conduct or block properly.
59 OVERVOLTAGE RELAY is a relay that functions on a given value of overvoltage.
60 VOLTAGE OR CURRENT BALANCE RELAY is a relay that operates on a given difference in voltage, or current input or output, of two circuits.

61 RESERVED FOR FUTURE APPLICATION.
62 TIME-DELAY STOPPING OR OPENING RELAY is a time-delay relay that serves in conjunction with the device that initiates the shutdown, stopping, or opening operation in an automatic sequence or protective relay system.
63 LIQUID OR GAS PRESSURE OR VACUUM RELAY is a relay that operates on given values of liquid or gas pressure or on given rates of change of these values.
64 GROUND PROTECTIVE RELAY is a relay that functions on failure of the insulation of a machine, transformer, Or of other apparatus to ground, or on flashover of a d-c machine to ground. Note: This function is assigned only to a relay that detects the flow of current from the frame of a machine or enclosing case or structure of a piece of apparatus to ground or detects a ground on a normally ungrounded winding or circuit. It is not applied to a device connected in the secondary circuit of a current transformer, or in the secondary neutral of current transformers, connected in the power circuit of a normally grounded system.
65 GOVERNOR is the assembly of fluid, electrical, or mechanical control equipment used for regulating the flow of water, steam, or other medium to the prime mover for such purposes as starting, holding speed or load, or stopping.
66 NOTCHING OR JOGGING DEVICE is a device that functions to allow only a specified number of operations of a given device, or equipment, or a specified number of successive operations within a given time of each other. It is also a device that functions to energize a circuit periodically or for fractions of specified time intervals, or that is used to permit intermittent acceleration or jogging of a machine .


Device Number Function and Description
67 A-C DIRECTIONAL OVERCURRENT RELAY is a relay that functions on a desired value of a-c overcurrent flowing in a predetermined direction.
68 BLOCKING RELAY is a relay that initiates a pilot signal for blocking of tripping on external faults on a transmission line or in other apparatus under predetermined conditions, or cooperates with other devices to block tripping or to block re-closing on an out-of-step condition or on power savings.
69 PERMISSIVE CONTROL DEVICE is generally a two position manually operated switch that, in one position, permits the closing of a circuit breaker, or the placing of an equipment into operation, and in the other position prevents the circuit breaker or the equipment from being operated.
70 RHEOSTAT is a variable resistance device used in an electric circuit, which is electrically operated or has other electrical accessories, such as auxiliary, position, or limit switches.
71 LIQUID OR GAS-LEVEL RELAY is a relay that operates on given values of liquid or gas level c on given rates of change of these values.
72 D-C CIRCUIT BREAKER is a circuit breaker that is used to close and interrupt a d-c power circuit under normal conditions or to interrupt this circuit under fault or emergency conditions.
73 LOAD-RESISTOR CONTACTOR is a contactor that is used to shunt or insert a step of load limiting, shifting, or indicating resistance in a power circuit, or to switch a space heater in circuit. It may be used to switch a light or regenerative load resistor of a power rectifier or other machine in and out of circuit.
74 ALARM RELAY is a relay other than an annunciator, as covered under device function 30, that is used to operate, or to operate in correction with, a visual or audible alarm.
75 POSITION CHANGING MECHANISM is a mechanism that is used for moving a main device from one position to another in equipment; for example, shifting a removable circuit breaker unit to and from the connected, disconnected, and test positions.
76 D-C OVERCURRENT RELAY is a relay that functions when the current in a d-c circuit exceeds a given value.
77 PULSE TRANSMITTER is used to generate and transmit pulses over a telemetering or pilot-wire circuit to the remote indicating or receiving device.
78 PHASE-ANGLE MEASURING OR OUT-OF STEP PROTECTIVE RELAY is a relay that functions at a predetermined phase angle between two voltages or between two currents or between voltage and current.
79 A-C RE-CLOSING RELAY is a relay that controls the automatic re-closing and locking out of an a-c circuit interrupter.
80 LIQUID OR GAS FLOW RELAY is a relay that operates on given values of liquid or gas flow or on given rates of change of these values
81 FREQUENCY RELAY is a relay that functions on a predetermined value of frequency (either under or over or on normal system frequency) or rate of change of frequency.
82 D-C RE-CLOSING RELAY is a relay that controls the automatic closing and re-closing of a d-c circuit interrupter, generally in response to load circuit conditions.


Device Number Function and Description
83 AUTOMATIC SELECTIVE CONTROL OR TRANSFER RELAY is a relay that Operates to select automatically between certain sources or conditions in equipment, or performs a transfer operation automatically.
84 OPERATING MECHANISM is the complete electrical mechanism or servomechanism, including the operating motor, solenoids, position switches, etc., for a tap changer, induction regulator, or any similar piece of apparatus which otherwise has no device function number.
85 CARRIER OR PILOT-WIRE RECEIVER RELAY is a relay that is operated or restrained by a signal used in connection with carrier-current or d-c pilot wire fault directional relaying.
86 LOCKING-OUT RELAY is an electrically operated hand, or electrically, reset relay or device that functions to shut down or hold an equipment out of service, or upon the occurrence of abnormal conditions.
87 DIFFERENTIAL PROTECTIVE RELAY is a protective relay that functions on a percentage or phase angle or other quantitative difference of two currents or of some other electrical quantities.
88 AUXILIARY MOTOR OR MOTOR GENERATOR is one used for operating auxiliary equipment, such as pumps, blowers, exciters, rotating magnetic amplifiers, etc.
89 LINE SWITCH is a switch used as a disconnecting, load-interrupter, or isolating switch in an a-c or d-c power circuit, when this device is electrically operated or has electrical accessories, such as an auxiliary switch, magnetic lock, etc.
90 REGULATING DEVICE is a device that functions to regulate a quantity, or quantities, such as voltage, current, power, speed, frequency, temperature, and load, at a certain value or between certain (generally close) limits for machines, tie lines or other apparatus.
91 VOLTAGE DIRECTIONAL RELAY is a relay that operates when the voltage across an open circuit breaker or contactor exceeds a given value in a given direction.
92 VOLTAGE AND POWER DIRECTIONAL RELAY is a relay that permits or causes the connection of two circuits when the voltage difference between them exceeds a given value in a predetermined direction. I can also cause these two circuits to be disconnected from each other when the power flowing between them exceeds a given value in the opposite direction.
93 FIELD-CHANGING CONTACTOR is a contactor that functions to increase or decrease, in one step, the value of field excitation on a machine.
94 TRIPPING OR TRIP-FREE RELAY is a relay that functions to trip a circuit breaker, contactor, or equipment, or to permit immediate tripping by other devices; or to prevent immediate re-closure of a circuit interrupter if it should open automatically even though its closing circuit is maintained closed.
95-99 USED ONLY IN SPECIFIC APPLICATION WHERE NO OTHER NUMBER IS SUITABLE
 