Does any one know of a code preventing stranded wire from being wrapped around a screw on devices? have hit wiring methods , receps , and any other place i could think of thanks.
110.3(b) ;)
But there is no code issue on this particularly. Unless it is UL listed for solid wire only.
I don't think I've ever seen a 15 or 20 amp switch or recep. that does not specifally allow solid or stranded in the listing. But I have had inspectors challenge it.
2012 White Book RTRT Receptacles:
TERMINALS
Terminals of 15 and 20 A receptacles not marked ??CO/ALR?? are for use with copper and copper-clad aluminum conductors only. Terminals marked ??CO/ALR?? are for use with aluminum, copper and copper-clad aluminum conductors.
Terminals of receptacles rated 30 A and above not marked ??AL-CU?? are for use with copper conductors only. Terminals of receptacles rated 30 A and above marked ??AL-CU?? are for use with aluminum, copper and copper-clad aluminum conductors.
Terminals marked ??75 C?? may be wired using the ampacities for conductors rated 75?C as well as conductors rated 60?C in Table 310.16 of the NEC.
Terminals of the wire-binding screw, setscrew, or screw-actuated back-wired clamping types are suitable for use with both solid and stranded building wires.
Terminals of a receptacle are permitted for use with Listed field-installed crimped-on wire connectors or an assembly, if so identified by the manufacturer.
A receptacle may also be provided with conductor leads with factory-installed crimped-on connectors. Such connectors may be either attached to the receptacle terminal or are provided with the receptacle in the smallest unit shipping container and are suitable for use with the terminal of the receptacle.
Screwless terminal connectors of the conductor push-in type (also known as ??push-in-terminals??) are restricted to 15 A branch circuits and are for connection with 14 AWG solid copper wire only. They are not intended for use with aluminum or copper-clad aluminum wire, 14 AWG stranded copper wire, or 12 AWG solid or stranded copper wire.
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
* Back-wire (screw-actuated clamp type) terminations with multiple wire-access holes used concurrently to terminate more than one conductor
* Side-wire (binding screw) terminals used concurrently with their respective push-in (screwless) terminations to terminate more than one conductor
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have not been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
* Side-wire (binding screw) terminal with its associated back-wire (screw-actuated clamp type) terminal
* Multiple conductors under a single binding screw
* Multiple conductors in a single back-wire hole
Duplex receptacles rated 15 and 20 A that are provided with break-off tabs may have those tabs removed so that the two receptacles may be wired in a multi-wire branch circuit or multiple branch circuits.