Devices in wireways.

What is it powering?

If it is allowed in there I'd say it likely shouldn't take up more than 75% of the cross section of the wireway, yet having a hard time finding any code to apply to anything but terminal blocks being in the wireway.

Are those conductors in there or cables? If all cables it maybe could be just treated as a general use housing to hold said equipment and cables. If art 310 conductors are in there then it is a wireway.
 
Those pictures on the left look to be of a NEMA 3 cabinet, not a wireway. Installing a receptacle within to power equipment is allowable.

I have no idea how it relates to the picture on the right or even what any of it is for.

-Hal
 