Jeff Fairfax
New member
I have run across this topic more than enough times, but, would like someone else's opinion. Installing a 1200 amp overcurrent device, many times customers, and or engineers request 3 runs of 500kcmil conductors. The code reads that anything 800 amperes or over must have conductors equal to or greater than o.c. rating. This would lead me to believe that 3 runs of 600 kcmil would be necessary to meet code. Since 3 runs of 500 kcmil is equivalent to 1140 amperes, it would be necessary to drop the o.c device to 1000 amperes. I've spoken to several local people about this and get the same reaction, "we've been installing 1200 amp services with 3 runs of 500 kcmil for years" is this wrong or am I misinterpreting this particular code article? I always get questions why my price is higher than my competitor when it comes to 1200 amperes services. Any thoughts?