DFCIs and GFCIs in shop applications?
fastline
midwest usa
Engineer
Working on two different shops right now. One is residential, one industrial, but both are certainly shop environments where we are "building new". For that reason, I am looking at certain safety tech that can optimize safety without compromising the shop. In a little research, it would seem even modern DFCIs can still be problematic with certain 'shop' type loads in receptacles? I realize in certain settings, none of this is really required, but I am trying to be proactive here as long as it does not create nothing but nuisance trips! Any other solutions or ideas, pitch them over.
dual function circuit breaker. Probably lots of lingo for them. Arc fault combined with ground fault. Standard issue in homes now.
The code term in 210.12 is combination AFCI. Dual function refers to an obsolete type of AFCI.
Most residential shop locations don’t require AFCI, but probably do require GFCI.
GFCI maybe required for industrial locations.
I mean, lets mud the waters up by calling them the same thing. I believe "combination" referred to the series and parallel arc faults.
I'm not really asking about code requirements as much as if these critters have proven reliable in the field.
No Tom, dual function is not obsolete, it is the newest breaker that combines AFCI & GFCI. Thus they are called "Dual function".
The obsolete one is the branch circuit AFCI and only did series(?). They changed that to combination, which means parallel and series faults.
AFCI is not required in industrial settings. Nor are they required in a dwelling garage/shop. No need for a DF breaker in these areas. A GFCI receptacle feeding downstream would be all that is needed, and cheaper.
Appreciate it! But again, I am not really combing code requirements, but trying to assess the practical use in a shop, regardless. There is most certainly some good reason for their use in these areas, but I would question if they would be tripping out all the time.
Ok. It is confusing. Cali it the device that is AFCI and gfci
I wouldn't use Arc Fault where not required, unless I was mad at the customer
Ha ha...
Note to self - stay on Dave's good side ;)
As to the OP - We had some receptacles in our industrial shop that were GFCI protected. I don't recall ever having a problem with them. I think one might have tripped a time or 2 - but it was always from flaky equipment being plugged in. It was just doing its job.