Diagram of Make up Air Unit

Status
Not open for further replies.

ianis

Member
Does anyone have a link to a diagram showing an interlock between a make up air unit model HE221/MV from EngA and a Exaust Fan? I need to interlock the make up air unit with the Fire alarm panel and the CO system in a parkade. I can go through designing my own interlocks using Isolation Modules, Ice cube relays and contactors however I would like to know if there is a diagram already made that would make my life easyer. tx
 
There's no single circuit. It depends on a bunch of stuff, such as: one or two switches, direct or contactor control, new or retro-fit, and about 20 different possibilities.

If you like, PM me for my phone number.
 
many curcuits to cut under hood...

many curcuits to cut under hood...

In the restaurant i'm doing, they have added and changed appliances. 6-120v (20 amp curcuits, 1 pole) one of which is for hood ltg. 2-208v (single phase 40 amp 2 pole) 1-208v (3 phase 50 amp). shunt breakers for this are totalling about $1500... I thought using 2 3 pole contactors, 1 4 pole contactor and another 3 pole contactor for the larger 3 phase unit would do... would using seperate enclosures; each with 1 contactor be viable? total of about 150 amps 3 phase to cut out...


Matt
 