I went on a service call yesterday that has me wondering.
Two story farm house with large workshop about 200' in rear. House had a 200 amp. service installed about 5 years ago. Garage was fed with a 3 wire 100 amp circuit to a 100 amp MBP.
Home owner had been having problems in the workshop. Furnace and frig, not running right, lights dimming, etc. He said he hadn't had any problems in the house. Sounded to me like a classic neutral problem with the feed to the workshop.
Since I was already in the warm house I decided to start there and didn't even go to the workshop. Pulled cover, all voltages seemed good. However, in moving wires around I could hear something sizzling. A connector had been over tightened on one of the branch circuits and a piece of 12/2 was burning. I pulled the effected cicuit and repaired. The neutral in the romex was pretty cooked.
Headed out to the workshop and everything is working fine now. I did notice that the sub-panel in the garage had no grounding bar. Everything including the ground rod was run to the neutal bar and panel was not bonded.
I wonder how what I did in the main panel fixed the problem in the workshop? I will be going back next week to seperate neutrals and grounds in the subpanel. Is there something else you would check here? Just wondering, thanks
Two story farm house with large workshop about 200' in rear. House had a 200 amp. service installed about 5 years ago. Garage was fed with a 3 wire 100 amp circuit to a 100 amp MBP.
Home owner had been having problems in the workshop. Furnace and frig, not running right, lights dimming, etc. He said he hadn't had any problems in the house. Sounded to me like a classic neutral problem with the feed to the workshop.
Since I was already in the warm house I decided to start there and didn't even go to the workshop. Pulled cover, all voltages seemed good. However, in moving wires around I could hear something sizzling. A connector had been over tightened on one of the branch circuits and a piece of 12/2 was burning. I pulled the effected cicuit and repaired. The neutral in the romex was pretty cooked.
Headed out to the workshop and everything is working fine now. I did notice that the sub-panel in the garage had no grounding bar. Everything including the ground rod was run to the neutal bar and panel was not bonded.
I wonder how what I did in the main panel fixed the problem in the workshop? I will be going back next week to seperate neutrals and grounds in the subpanel. Is there something else you would check here? Just wondering, thanks