For as long as I have been designing solar (~14 years) I have been using the John Wiles method for selecting 90 degree AC conductors, which is to pick a conductor that will a) carry 125% of the maximum inverter current at 75 degrees AND b) carry 100% of the inverter current after derating for conditions of use (ambient temperature and conduit fill) at 90 degrees. Calculation a) is to protect 75 degree terminals under continuous use and calculation b) is for 90 degree wiring insulation preservation.
I am reviewing a design done by someone else which shows AC conductors one size smaller than I would have chosen, and it is done under the 2020 NEC, so to exercise due diligence I have gone to 690.8(B), and I do not see anything about protecting 75 degree terminals. Did the rules change? Is everything I know wrong?
I am reviewing a design done by someone else which shows AC conductors one size smaller than I would have chosen, and it is done under the 2020 NEC, so to exercise due diligence I have gone to 690.8(B), and I do not see anything about protecting 75 degree terminals. Did the rules change? Is everything I know wrong?