I am looking for a minimum current leakage I should use for a pass/fail value in a hi-pot test. I am testing with respect to creep over a flat surface on which there is potential for settling of hygroscopic chemical residue. I've checked in UL standards and a few different google searches, but I'm struggling to find a pass/fail threshold, and the justification for that value.
System is 480V with ground and neutral. Test instrument has a max of 5mA trip. I plan to use a 1 second ramp to 3000VAC with a 1 minute dwell. 60Hz.
I am creating a test plan to investigate the most effective means of insulating a 3 phase w/gnd plug using butt contacts to combat creep leakage over the surface of a plug in a mild to harsh chemical wash down environment. The device is already IP69 rated. no presence of explosive atmosphere. I can provide more application information if you wish, but for now, that may just be "noise".
I'm new to the forum (first post), so apologies if this answer is floating out there elsewhere. I've looked but the keywords I'm searching are not hitting.
System is 480V with ground and neutral. Test instrument has a max of 5mA trip. I plan to use a 1 second ramp to 3000VAC with a 1 minute dwell. 60Hz.
I am creating a test plan to investigate the most effective means of insulating a 3 phase w/gnd plug using butt contacts to combat creep leakage over the surface of a plug in a mild to harsh chemical wash down environment. The device is already IP69 rated. no presence of explosive atmosphere. I can provide more application information if you wish, but for now, that may just be "noise".
I'm new to the forum (first post), so apologies if this answer is floating out there elsewhere. I've looked but the keywords I'm searching are not hitting.