acraig
New User
- Location
- Chilhowie, VA
- Occupation
- Electrical Design Enginner
I'm designing a generator system for a WWTP. The generator size will be 750-kW with a 24-hour runtime (approximately 1700 gallons).
The generator will be located outside near the building with the electrical distribution equipment. I'm trying to determine how far off the building I need to be.
I'm mainly finding a minimum of 5 feet through various sources. I've been told to look at NFPA 30, specifically chapter 17. Table 17.4.3 would place me a minimum of 25 feet off the building. Does anyone know the applicability of NFPA specifically, chapter 17, to diesel generators?
Any information would be helpful!
Thanks.
The generator will be located outside near the building with the electrical distribution equipment. I'm trying to determine how far off the building I need to be.
I'm mainly finding a minimum of 5 feet through various sources. I've been told to look at NFPA 30, specifically chapter 17. Table 17.4.3 would place me a minimum of 25 feet off the building. Does anyone know the applicability of NFPA specifically, chapter 17, to diesel generators?
Any information would be helpful!
Thanks.