can dlc be installed in conduit as feeders. or can dlc cable be installed anywhere according to the 2008 nec.
Yes, the DLO has nonstandard sizing and there is no code amapcity for those nonstandard sizes. We use the ampacity of the next smaller "code" size conductor when sizing DLO/RHW conductors. You can't use the manufacturer's listed ampacity as that is almost always a 90?C free air ampacity.And most case the DLO cable useally have nonstandard size and the numbers of strands is much finer than common building conductors are.
Merci,
Marc
Yes, the DLO/RHH does not come in code standard sizes and there is no code ampacity for those conductors. We use the ampacity of the next smaller "code" size conductor when we selected the ampacity of DLO conductors.
You can't use the manufacturer's ampacity as that is a 90?C free air ampacity.