wastewateguy
New member
- Location
- Toronto, Ontarion, Canada
We are replacing a diesel driven pump in a sewage bypass pump station. The pump is manually activated in case of high flows reaching the wastewater treatment plant. The station is old and has not been designed to meed the NFPA 820 requirements. The station is a wet well/dry well confirguration and the pump and engine are located in the dry well, with the pump below grade and the diesel engine above grade. There is no separation between the basement (where the pump is) and the ground floor where the diesel engine sits. We are intending to classify the entire space as Class 1 Div 2 since continuous ventilation would need to be hooked up to stand by power - which does not exist and will not fit on the site. It is also a waste of money bearing in mind that this station is only operated very intermittently. All electrical and control equipment will be replaced with components suitable for use in a Class 1 Div 2 location. My first question is: Is it possible to locate a diesel engine in a Class 1 Div 2 location or will it need to be modified to suit? Second question: Bearing in mind that the pump is only initiated manually in a severe storm event, a combustible gas detector would indicate if the conditions were safe to operate the pump - would this be a compliant approach? Final Question: Would we be better off trying to obtain a variance from the jurisdiction having authority. NOTE: This facility is in Ontario Canada and while we have our own electrical code, it generally defers to NFPA 820 for wastewater plants. Thanks in advance.