Diesel standby generator testing

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
What is the proper way to test diesel genets? Currently my understanding is weekly no load tests at 15 minutes and 6 month tests under load bank at the standby rating for at least 90 minutes to prevent wet stacking.
 
I have all of the generators I am responsible for set to test weekly for 20 min. under load. Then I load bank them every year. Running a diesel unit under a no load condition will wet stack it quicker. With no load the engine usually will not get up to operating temperature to even open the thermostat in the engine.
 