I've had a question about the wiring requirements for an above ground diesel storage/filling tank. I've poured over the 500 articles in the 2017 NEC and cannot find anything that seems to address this question.

The pump needs 120v circuit and I don't know if any special requirements are needed. I welcome any input on this matter.

Thank you,

Norb
 

d0nut

Senior Member
Location
Omaha, NE
Diesel fuel does not make a classified (hazardous) area. No special requirements from the 500 articles would apply. Now if you ever want to put gasoline in your storage tank, that would require special wiring methods.
 