First post here so go easy on me. I work for an electrician and we do mostly residential rewire type stuff. There have been a few times when we have added subpanels by just tee splicing (polaris connectors) into the feeder cable in an approved box. Both times the splice has only been protected by the main panel breaker (sized appropriately for the feeder) and the ampacity of the wire has remained the same. For some reason this seems weird to me but the guy I work for says it is fine but not the best way to do it / sometimes unavoidable. My question is, Is this considered a tap which tap rules would apply to or is it okay to tee splice into a feeder so long as load considerations are okay. Does each subpanel require it's own breaker or does it matter since the main breaker is protecting it and the wire is not different sizes before or after the splice/tap? I am getting hung up on the tap rule versus the defintion of a splice. Based on the definition of a tap, does using the same wire on all three sides of the tee make it okay so long as the wire does not exceed the protection in front of it?
An example of the above, the last one we did.
Small apartment building where we added a subpanel in the garage to one of the units. The main breaker was a 60 amp breaker off a meter stack which feeds a sub in the apartment via 6/3 copper. No space on the meter stack for additional breakers since it is only a main disconnect for each units sub panel. Rather than open walls in multiple apartments to get to that particular units subpanel, we just tee spliced the 6/3 under the building with 3 way polaris connectors in a 6x6x4 box and ran 6/3 to another subpanel that only had a few circuits on it.
Section 240 definition of a tap
. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply, that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4
An example of the above, the last one we did.
Small apartment building where we added a subpanel in the garage to one of the units. The main breaker was a 60 amp breaker off a meter stack which feeds a sub in the apartment via 6/3 copper. No space on the meter stack for additional breakers since it is only a main disconnect for each units sub panel. Rather than open walls in multiple apartments to get to that particular units subpanel, we just tee spliced the 6/3 under the building with 3 way polaris connectors in a 6x6x4 box and ran 6/3 to another subpanel that only had a few circuits on it.
Section 240 definition of a tap
. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply, that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4