wirenut1980
Senior Member
- Location
- Plainfield, IN
Hi everyone, I am looking at the Square D relay overload selection catalog which can be seen here. I am troubleshooting for a customer that has a well pump motor that runs for about 10 minutes and then the overload relay shuts the motor down. The overload relay is a Square D bimetallic E80. Right before shutdown the current waveform peak current was 120 Amps, which gives an RMS value of about 84.9 amps. The motor has been refurbished and the nameplate full load current is 65 Amps.
The E80 thermal unit number is listed several times in the lookup tables next to different corresponding full load current ranges. What is the difference and how to tell which one is installed at the motor?
Btw, current and voltage waveforms did not show anything out of the ordinary that would cause the relay to trip.
The E80 thermal unit number is listed several times in the lookup tables next to different corresponding full load current ranges. What is the difference and how to tell which one is installed at the motor?
Btw, current and voltage waveforms did not show anything out of the ordinary that would cause the relay to trip.