Difference between SCCR and AIC Rating

Status
Not open for further replies.

mathan1987

Member
Location
Seattle
Occupation
Electrical design engineer
What is the difference between SCCR and AIC rating?
where to use them ? How to calculate them.? NEC articles related to the SCCR/ AIC Rating ?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
SCCR is the amount of fault current a piece of equipment can withstand. AIC rating is the amount of fault current and overcurrent device can withstand.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you have a pdf of the nec search for available fault current. You wont find anything under aic or sccr. Here is one area where the nec talks of available fault current

110.24 Available Fault Current.
(A) Field Marking. Service equipment at other than dwelling
units shall be legibly marked in the field with the maximum
available fault current. The field marking(s) shall include the
date the fault-current calculation was performed and be of
sufficient durability to withstand the environment involved.
The calculation shall be documented and made available to
those authorized to design, install, inspect, maintain, or operate
the system.
Informational Note: The available fault-current marking(s)
addressed in 110.24 is related to required short-circuit current
ratings of equipment. NFPA 70E -2015, Standard for Electrical
Safety in the Workplace, provides assistance in determining the
severity of potential exposure, planning safe work practices, and
selecting personal protective equipment.
(B) Modifications. When modifications to the electrical installation
occur that affect the maximum available fault current at
the service, the maximum available fault current shall be verified
or recalculated as necessary to ensure the service equipment
ratings are sufficient for the maximum available fault
current at the line terminals of the equipment. The required
field marking(s) in 110.24(A) shall be adjusted to reflect the
new level of maximum available fault current.
Exception: The field marking requirements in 110.24(A) and
110.24(B) shall not be required in industrial installations where conditions
of maintenance and supervision ensure that only qualified
persons service the equipment.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Basically 110.09 deals with AIC, it says protective devices must be rated for the fault current at their line side terminals.
In a similar manner 110.10 deals with the SCCR of equipment.
 