Difference between System Bonding Jumper and Main Bonding Jumper

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Can someone explain the difference between these two animals. The system jumper seems to add "at a separately derived system" but aren't all services a separately derived system.


Bonding Jumper, Main. (Main Bonding Jumper)
The connection between the grounded circuit conductor and the equipment grounding conductor, or the supply-side bonding jumper, or both, at the service. (CMP-5)

Bonding Jumper, System. (System Bonding Jumper)
The connection between the grounded circuit conductor and the supply-side bonding jumper, or the equipment grounding conductor, or both, at a separately derived system. (CMP-5)


1729953891253.png
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Can someone explain the difference between these two animals.
The only difference is the MBJ is at a service, and an SBJ is not. The difference is terminological, not electrical.

The system jumper seems to add "at a separately derived system" but aren't all services a separately derived system.
No, per the definition:

Separately Derived System. An electrical source, other than a service, having no direct connection(s) to circuit conductors of any other electrical source other than those established by grounding and bonding connections.

Cheers, Wayne
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It sounds to me like the basic difference is the SBJ is a the point of the system origin (transformer secondary), and the MBJ is at the point of use (premises service). Kinda theirs vs ours.

The former establishes the source as a grounded system, and the latter establishes the EGC pathway.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Another difference is that a service may be actually bonded (and grounded) elsewhere than at the MBJ. (e.g. meter socket) An SDS is not supposed to be.
 