Here is my question - we have 2 different industrial recycling lines. I am using a fluke 376c meter
There is a 2000a MDP 480v 4w
We have a 10 section 26 motor MCC
5 total vfd's 2 powerflex 525 and 3 powerflex 755
1 - 422hp motor
1 - 177hp motor
1 - 40hp motor
When i use my meter to read the total draw on this equipment i am reading 134amps each phase. The readings from each vfd and mcc are totaling 400+ amps.
I can read 175a on the load side of the 422hp motor vfd without a load and on the line side i read 30amps each phase. Can anyone help me out with what is going on? I know the readings we are getting on the load side are correct but why is the line side so low?? In Speaking to a engineer he said our voltage and current are out phase and the PF is our problem. We other engineers who dont seem to be concerned with the problem.
Here is my question - we have 2 different industrial recycling lines. I am using a fluke 376c meter
There is a 2000a MDP 480v 4w
We have a 10 section 26 motor MCC
5 total vfd's 2 powerflex 525 and 3 powerflex 755
1 - 422hp motor
1 - 177hp motor
1 - 40hp motor
When i use my meter to read the total draw on this equipment i am reading 134amps each phase. The readings from each vfd and mcc are totaling 400+ amps.
I can read 175a on the load side of the 422hp motor vfd without a load and on the line side i read 30amps each phase. Can anyone help me out with what is going on? I know the readings we are getting on the load side are correct but why is the line side so low?? In Speaking to a engineer he said our voltage and current are out phase and the PF is our problem. We other engineers who dont seem to be concerned with the problem.