We have an existing feeder with (2) sets of 3-1/2" RMC. The load increased and required a third set of conductors. The contractor added a third conduit run of 3-1/2" IMC.
2023 NEC 310.10(G)(3) states that: "Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics."
I'm interpreting "electrical characteristics" to mean the type of material the conduit is made of. For example, aluminum vs. steel or steel vs. pvc, would not be allowed.
For my situation, wouldn't IMC and RMC have the same "electrical characteristics" since they are both rigid steel conduits?
2023 NEC 310.10(G)(3) states that: "Where run in separate cables or raceways, the cables or raceways with conductors shall have the same number of conductors and shall have the same electrical characteristics."
I'm interpreting "electrical characteristics" to mean the type of material the conduit is made of. For example, aluminum vs. steel or steel vs. pvc, would not be allowed.
For my situation, wouldn't IMC and RMC have the same "electrical characteristics" since they are both rigid steel conduits?