It depends on what size over current device is protecting it. 30A to 60A, use #10. 70A to 100A, use #8. NM cable is limited to 60C, so 55A ampacity and maybe a 60A breaker at most. MC cable is probably 75/90C, so it would have an ampacity of 65A in #6 cu and could be on a 70A breaker.
 
Why is romex #6-3 ground wire size 10 and MC cable ground wire size #8 ?
As they said above, conductors in MC have a higher ampacity than in NM for a given size.

for running conductors in conduit, which size should I use ?
That depends on the load current. MC cable and individual wires have the same ampacity.
 