So i just did a service change for a solar contractor and I used #4 Cu for the ground rods and also for the water pipe ground. Solar guy is telling me I need #6 for the water bond and #4 to the ground rods.
This doesn't make any sense to me. I have it sized correctly according to incoming feeder size. But an equipotential plane has to exist in the grounding system. All wires have to be the same size to there is an equalizing. Am i missing something?