What determines the size of a service? Or can "service size" actually be an ambiguous term?
For example, per Art 230, service conductors must be at least sized on load and 220 calcs, and similar with the service disconnect rating. And the service OCPD per 230.90 specifies that it must protect the service conductors.
So what if I have this (all 480/277V):
Utility transformer is 1000kVA, so roughly 1200A
Service conductors with ampacity of 1400A
Service disconnect with bus rating of 1600A
Service OCPD is 1600A breaker, but is adjustable to be set to 1400A
What size is this service? 1200A? 1400A, 1600A?
I don't actually have this situation, but I realized I don't know the answer to this. I just picked these numbers randomly. And perhaps this isn't even a valid possibility that this could occur.