We just had a problem with a transformer.
The 69 kV primary side multi tap CT's were wired so the connections to the 100:5 tap would go to the relay.
One side was grounded as recommended and ALL unused taps were also jumpered and grounded.
The percent differential relay tripped at 30% like it was programmed to trip.
The secondary CT's operated fine, they were reading current in the differential meter.
The W1 primary CT's were NOT reading current.
When the differential relay tripped off line the event recorder recorded current for W1, a,b&c,
but all other events had "0" current recorded on the W1 on the high side ct's.
We resolved the problem by relocating the ground wires and unshorting the unused terminals and the primary ct's read correctly. W1 current matches W2 winding current and shows up in the meter.
No one can tell me why open circuiting the unused CT's on a multi tap ct will cause the CT to transfer current to the relay and having the unused taps shorted will not pass current.
Any ideas?
I hear theories but no one has paperwork to back it up.
"They say it is done all of the time."
Everything I have read states that the CT secondary must be shorted to prevent high voltages from being created across an open terminal when current is flowing. I have seen open circuited CT's start a fire in switchgear.
The 69 kV primary side multi tap CT's were wired so the connections to the 100:5 tap would go to the relay.
One side was grounded as recommended and ALL unused taps were also jumpered and grounded.
The percent differential relay tripped at 30% like it was programmed to trip.
The secondary CT's operated fine, they were reading current in the differential meter.
The W1 primary CT's were NOT reading current.
When the differential relay tripped off line the event recorder recorded current for W1, a,b&c,
but all other events had "0" current recorded on the W1 on the high side ct's.
We resolved the problem by relocating the ground wires and unshorting the unused terminals and the primary ct's read correctly. W1 current matches W2 winding current and shows up in the meter.
No one can tell me why open circuiting the unused CT's on a multi tap ct will cause the CT to transfer current to the relay and having the unused taps shorted will not pass current.
Any ideas?
I hear theories but no one has paperwork to back it up.
"They say it is done all of the time."
Everything I have read states that the CT secondary must be shorted to prevent high voltages from being created across an open terminal when current is flowing. I have seen open circuited CT's start a fire in switchgear.