I have a situation where a college owns the medium voltage service equipment on their facility. The PCO has completed their service to the 2 separate 2000 amp 12.47kv medium volt switchgear. These two sections of gear then feed two pad mounted 3750 12.47kv/480/277v transformers also owned by the college. So all service equipment is owned by the college. The Utility only has provided the service drop.
Now here is the area where I am unclear about...
The two pad mounted transformers then each feed switchgear in the building. There are 12 parallel 600 KCMIL (4 per conduit) feeds from each xfmer to the swithgear at which point the neutral will be grounded. This seems like a typical commercial service arrangement but...
We are being told to add equipment grounding conductors to the service conduits (24 total) entering into the building. I am confused to why I need to do this. Besides there is no place in the service transformers to terminate the ground conductors. We are being told to refer to NEC 2011 Articles 230.200 and 230.31. They are also refering to NEC Article 225 Part II because we have parking garage and another building being served by this service.
Any help here?
Now here is the area where I am unclear about...
The two pad mounted transformers then each feed switchgear in the building. There are 12 parallel 600 KCMIL (4 per conduit) feeds from each xfmer to the swithgear at which point the neutral will be grounded. This seems like a typical commercial service arrangement but...
We are being told to add equipment grounding conductors to the service conduits (24 total) entering into the building. I am confused to why I need to do this. Besides there is no place in the service transformers to terminate the ground conductors. We are being told to refer to NEC 2011 Articles 230.200 and 230.31. They are also refering to NEC Article 225 Part II because we have parking garage and another building being served by this service.
Any help here?