I am cost estimating a job for a sleeping facility for a large group of people. The facility is made of brick and much of the inside walls are concrete also. There is only 8 inches of crawl space above the ceiling between floors as you will again hit concrete.
I need to add another breaker to be distributed to the receptacles in each room since the receptacles are overloaded now with hair dryers, hot pans, microfridges, computers, microwaves, TVs, Boom Boxes, etc. The panelboards are too full to add a new breaker for each room.
I need to add some new 400 amp and 225 amp 3 phase, 208/120 volt panelboards.
The only way to do this is pull all the cable out between the existing receptacles and the existing panel boards, then rewire all the panelboards and wire tne new panelboard as I see it to include a new feeder for the new panelboard.
I would think the electricians may have a hard time pulling all that cable out of the existing conduit and putting new #12 cable in the conduits to feed the receptacles when dealing with concrete wallw and no crawl spaces to fish cable. Am I right??? If so, I will estimate tearing out a lot of wall and ceiling to do this job??