electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
- Occupation
- Electrician
We have a 14.625KW ground mount, 45 325W 96 cell panasonic modules. We have two sunny boy 7.7 inverters (6 MPPT inputs total) Long story short, the original modules planned were destroyed in shipment, and this is what we have now. The problem is the temperature corrected VOC allows only 7 modules per string, so that is 42 modules. We discussed, and decided to get 3 sunny boy 5.0 inverters, however there were delays in those and we jut found out they havnt even shipped yet. We dont have much time to finish this system so have scrapped that idea. One option we are looking at is 3 strings of 7 to one inverter, and 4 strings of 6 connected to the other inverter with two of those connected in parallel. The other idea is to use a third 7.7 inverter (which we do have) and do 9 strings of 5. Obviously there is a cost to providing a 3rd inverter for a system originally designed and priced for 2. I minor advantage of the 3, besides the increased number of MPPT's, is stringing is real nice because the array is 9 rows of 5 so all connections can be at the top end. Any thoughts on these two options or anything else that maybe I havnt thought of?