Digital Meter

Carlosu12

New User
Location
Cebu City, Philippines
Occupation
Building Engineer
dayprevious (kwh)current (kwh)consumption (kwh)
day 1969.9975.75800
day 2975.7981.76000
day 3981.7988.77000
day 4988.7994.86100
day 5994.81.001?
day 61.0011.008?

Hi All, good day. Need clarification on how to interpret readings for our power meter. Made by LS Electric, the GMAC1000. Above are some of the meter readings for kwh. In all of these readings, the "X1000" indicator light is ON. In day1 to day4, it's pretty straightforward, we just multiply the values by 1000 (as indicated by "X1000") to get the consumption or subtract the "previous" from the "current" readings then multiple the result by 1000.
But for day 5, does the meter rolled-over? And from then on, we have to multiply by a million instead of a thousand? And the next roll-over, multiply by a billion?
Hope to be enlightened. Thanks.
 