Two year old 800Amp 480/277v main has opened randomly now twice.
Facility is very lightly loaded at the time [weekend night].
Normally has much more HVAC and pools loads when occupied.
Opening main sends fire alarm notifier to director of operations and cops.
Director sees no reason main should be off and resets. Just fine.
Next day same thing, but he calls me before reseting.
I went with him that night in my PPE and we opened it up and looked for arcing/discolor, measured temperature and voltage. Couldn't clamp amps on the buswork but I only clamped less than 50 amp of load mostly pool pumps.
Engineer's dials show
ST: pickup is at max which is 8
ST: time is min = INST
GF: pickup min 1
GF: time min INST
We have had problems with these new breakers giving nuisance tripping.
We have another 1200AMP 12Kv cabinet that really likes the loads to come back in a certain order.
I would love to be there quickly after cb opens to see if the thermal delay calls it an overload or a faulty load that just pulls the main before the subbreaker.
Question is why only intermittently? Faulty motor comes only sporadically?
There is a tester [and a qualified test person] who can plug in and read the digitrips report.
In the short term, and I don't want to take the fire responsibility for this, isn't the theory that you can "crank up" the dial on the main and this way the fault [if there is on] will show on the sub breakers?
Any insides?
Digitrip RMS 310
Facility is very lightly loaded at the time [weekend night].
Normally has much more HVAC and pools loads when occupied.
Opening main sends fire alarm notifier to director of operations and cops.
Director sees no reason main should be off and resets. Just fine.
Next day same thing, but he calls me before reseting.
I went with him that night in my PPE and we opened it up and looked for arcing/discolor, measured temperature and voltage. Couldn't clamp amps on the buswork but I only clamped less than 50 amp of load mostly pool pumps.
Engineer's dials show
ST: pickup is at max which is 8
ST: time is min = INST
GF: pickup min 1
GF: time min INST
We have had problems with these new breakers giving nuisance tripping.
We have another 1200AMP 12Kv cabinet that really likes the loads to come back in a certain order.
I would love to be there quickly after cb opens to see if the thermal delay calls it an overload or a faulty load that just pulls the main before the subbreaker.
Question is why only intermittently? Faulty motor comes only sporadically?
There is a tester [and a qualified test person] who can plug in and read the digitrips report.
In the short term, and I don't want to take the fire responsibility for this, isn't the theory that you can "crank up" the dial on the main and this way the fault [if there is on] will show on the sub breakers?
Any insides?
Digitrip RMS 310